We may be doing a paver ramp to a home for a wheelchair-bound person, and looked into the ADA specs for ramps, and found them. For those interested, here's the specs for a ramp:

Quote:
4.8 Ramps.

4.8.1* General. Any part of an accessible route with a slope greater than 1:20 shall be considered a ramp and shall comply with 4.8.

4.8.2* Slope and Rise. The least possible slope shall be used for any ramp. The maximum slope of a ramp in new construction shall be 1:12. The maximum rise for any run shall be 30 in (760 mm) (see Fig. 16). Curb ramps and ramps to be constructed on existing sites or in existing buildings or facilities may have slopes and rises as allowed in 4.1.6(3)(a) if space limitations prohibit the use of a 1:12 slope or less.

4.8.3 Clear Width. The minimum clear width of a ramp shall be 36 in (915 mm).

4.8.4* Landings. Ramps shall have level landings at bottom and top of each ramp and each ramp run. Landings shall have the following features:

(1) The landing shall be at least as wide as the ramp run leading to it.

(2) The landing length shall be a minimum of 60 in (1525 mm) clear.

(3) If ramps change direction at landings, the minimum landing size shall be 60 in by 60 in (1525 mm by 1525 mm).

(4) If a doorway is located at a landing, then the area in front of the doorway shall comply with 4.13.6.

4.8.5* Handrails. If a ramp run has a rise greater than 6 in (150 mm) or a horizontal projection greater than 72 in (1830 mm), then it shall have handrails on both sides. Handrails are not required on curb ramps or adjacent to seating in assembly areas. Handrails shall comply with 4.26 and shall have the following features:

(1) Handrails shall be provided along both sides of ramp segments. The inside handrail on switchback or dogleg ramps shall always be continuous.

(2) If handrails are not continuous, they shall extend at least 12 in (305 mm) beyond the top and bottom of the ramp segment and shall be parallel with the floor or ground surface (see Fig. 17).

(3) The clear space between the handrail and the wall shall be 1 - 1/2 in (38 mm).

(4) Gripping surfaces shall be continuous.

(5) Top of handrail gripping surfaces shall be mounted between 34 in and 38 in (865 mm and 965 mm) above ramp surfaces.

(6) Ends of handrails shall be either rounded or returned smoothly to floor, wall, or post.

(7) Handrails shall not rotate within their fittings.

4.8.6 Cross Slope and Surfaces. The cross slope of ramp surfaces shall be no greater than 1:50. Ramp surfaces shall comply with 4.5.

4.8.7 Edge Protection. Ramps and landings with drop-offs shall have curbs, walls, railings, or projecting surfaces that prevent people from slipping off the ramp. Curbs shall be a minimum of 2 in (50 mm) high (see Fig. 17).

4.8.8 Outdoor Conditions. Outdoor ramps and their approaches shall be designed so that water will not accumulate on walking surfaces.
The rest of the standards for ADA accessible design can be found here.

That's your answer. Here's your question: Does residential work fall under the purveyance of the ADA act?
Reply With Quote
  #2 (permalink)  
Old 08-29-2007, 03:18 PM
EpicInterlock's Avatar
Seedling
 
Join Date: Sep 2006
USDA Zone 10
Posts: 96
EpicInterlock is an unknown quantity at this point
I'm not 100% sure, but common sense would tell me ABSOLUTELY!!
__________________
Matt Blanche
Epic Interlock and Landscape
www.epicinterlock.com
Reply With Quote
  #3 (permalink)  
Old 08-29-2007, 03:30 PM
PaverDrew's Avatar
Gold Oak Member
 
Join Date: Apr 2005
USDA
Posts: 28
PaverDrew is an unknown quantity at this point
ADA applies public facilities, federal, state and local, and private properties accessible to the public, such as commercial properties for office, retail use, etc. I believe that ADA does not rule unless this property were to become a rental advertised with handicapped access.
Local ordinance could come into play, but most generally revert to the ADA. I am only an installer, not a compliance attorney, but this is how it has been explained to me.
Reply With Quote
  #4 (permalink)  
Old 08-29-2007, 07:04 PM
agla's Avatar
Gold Oak Member
 
Join Date: Feb 2003
Location: Cape Cod
USDA Zone 6
Posts: 1,319
agla is on a distinguished road
My understanding is the same as paverdrew's.

I'd stick to ADA standards to CYA and document any nonconforming things in writing to the client and keep a record of it. These standards make for expense. Homeowners who don't need to meet these standards might have you stray from them inorder to control costs. That is fine, but you have to document that they knowingly accepted these changes. When you build something like this and something happens to someone on the ramp, an argument could be made that ADA should have been the default standards to follow even if it was only implied.

If at all possible, try to keep below 5%. It is the best way to save on expense and negative aesthetics. But, it ain't easy to do.

I'm going to post a 5% ADA access on a new thread.
__________________




Cape Cod Landscape Architect
Reply With Quote
  #5 (permalink)  
Old 08-29-2007, 11:26 PM
EpicInterlock's Avatar
Seedling
 
Join Date: Sep 2006
USDA Zone 10
Posts: 96
EpicInterlock is an unknown quantity at this point
Put it this way.....if ADA is acceptable in commercial and public facilities which generally have very strict guidelines, then it should be more than good enough for a residential job
__________________
Matt Blanche
Epic Interlock and Landscape
www.epicinterlock.com
Reply With Quote
Reply


Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Question neversatisfiedj Hardscaping 0 07-24-2006 10:33 AM
Dynascape question PSUscaper Landscaping Design 24 07-01-2006 11:33 PM
Question On Flagstone Walk P-Train Hardscaping 4 08-08-2004 12:19 AM
Boulder wall question CuLayTur Hardscaping 4 04-05-2004 12:40 PM
Pond liner question chesie Hardscaping 4 04-05-2004 11:05 AM

All times are GMT -4. The time now is 01:00 PM.


Powered by vBulletin® Version 3.6.8
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Optimization by vBSEO 3.1.0
Copyright ©2003-2007 Ground Trades Xchange, LLC